[Equest-users] Data Center Server Heat Load - 3.63
John Aulbach
jra_sac at yahoo.com
Mon Sep 14 08:11:38 PDT 2009
Hi Greg:
You reached the Nirvana of eQuest information. If my solution isn't the best for you, some other esteemed member will give you his or hers.
Is your server load cooled by DX units or chilled water? If DX, you probably want the server load only satisfied by the DX units, not the other HVAC units in the space. eQuest (DOE-2 engine) cannot have tow systems satisfying one load.
For this situation, I would divide up the room into two zones. The first being the actual space dimensions, mius the server space. In this space, put your DX/chilled water HVAC unit. In the 2nd space, use the server sq.ft and add the server load as Process Load, to be satisfied by the Server HVAC
If your server is cooled by chilled water, I believe it should be the same procedure. However, the process load could be placed directly on the Chilled Water loop as a load. No HVAC required for the server space.
Others may have a more elegant solution.
John Aulbach
--- On Mon, 9/14/09, Ryerson, Gregory <Gregory.Ryerson at savvis.net> wrote:
From: Ryerson, Gregory <Gregory.Ryerson at savvis.net>
Subject: [Equest-users] Data Center Server Heat Load - 3.63
To: equest-users at lists.onebuilding.org
Date: Monday, September 14, 2009, 7:50 AM
I’m a newbie with eQuest and can’t determine how to add server load to my bldg. The ‘Heat Rejection’ and ‘Refrigeration’ sections are all zeroes after a simulation. Where do I add that load so that the HVAC will see the heat load? Thanks, Greg
Greg Ryerson | Facilities Engineer
Savvis
12301 Tukwila International Blvd, Tukwila , WA 98168
Office: 206.988.6545 | Mobile: 206.391.5813 | Fax: 206.835.8526
E-mail: gregory.ryerson at savvis.net
This message contains information which may be confidential and/or privileged. Unless you are the intended recipient (or authorized to receive for the intended recipient), you may not read, use, copy or disclose to anyone the message or any information contained in the message. If you have received the message in error, please advise the sender by reply e-mail and delete the message and any attachment(s) thereto without retaining any copies.
-----Inline Attachment Follows-----
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090914/c28b660c/attachment.htm>
More information about the Equest-users
mailing list