[Equest-users] oa from system
Verena Kindl
kindl at scholze.de
Wed Sep 2 05:52:55 PDT 2009
Hi,
as i now can define two different loops to my IU system is there a way to specify two different hot water coil delta T for the loops cause I can enter only one hot water coil delta T ? That is why I wanted to assign two different loops cause they have different delta T. And is there a way to assign a two different chilled water loops as well?
Thanks
Verena
________________________________
Von: Bishop, Bill [mailto:wbishop at pathfinder-ea.com]
Gesendet: Dienstag, 1. September 2009 14:49
An: Verena Kindl; equest-users at lists.onebuilding.org
Betreff: RE: [Equest-users] oa from system
Verena,
You should be able to assign different loops to the system-level and zone-level coils:
Regards,
William Bishop, EIT, LEED® AP | Pathfinder Engineers & Architects LLP
Mechanical Engineer
134 South Fitzhugh Street
Rochester, NY 14608
T: (585) 325-6004 Ext. 114
F: (585) 325-6005
wbishop at pathfinder-ea.com
www.pathfinder-ea.com
P Please strive to live sustainably.
________________________________
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Verena Kindl
Sent: Tuesday, September 01, 2009 8:14 AM
To: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] oa from system
Thanks Josh, but I already tried to model a IU unit but i have a different temperature range of the coils for the main AHU (90/50°C) and the coils of the FC (45/36°C) and I can not assign to different loops to the IU. So I am still trying.
________________________________
Von: Joshua Wolfe [mailto:jwolfe at geo-marine.com]
Gesendet: Dienstag, 1. September 2009 14:11
An: Verena Kindl; equest-users at lists.onebuilding.org
Betreff: RE: oa from system
Try a system type of IU, with the induction ratio matching that of the FCs. The main system then needs to be set to 100% OA with constant cool and heat control set to 68F. You will have to fake in extra fan power to match that of the FCs. Hope this helps.
Josh
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Verena Kindl
Sent: Tuesday, September 01, 2009 3:15 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] oa from system
Hello,
I have a SZRH system which should provide outside air to the FC system. The air it provides should always be 68 F. What temperatures shall I put for cooling design and heating design / thermostat setpoint T. I put min supply temp and max supply temp to 68 F and the other design temperatures to 53/90F cause I do not have a thermostat there ( the air is always provided with 68 F). Then I specified the OA constant to 4000 cfm and determined the min outside air ratio =1. Is there sth wrong with my temperature settings as I do not get any coil loads for the system (SS-J report)? When I set all temperatures to 68 F the ventilation air I require is too huge. Do I have to put the min OA ratio to 1, 0 or shall I leave it blank for the FC system? I mean is it enough to put OA from system SZRH? Cause someone told me I have to put it to 0 as I do not have any outside air put I do it is from the system. I am confused.
Thanks for your help.
Verena
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090902/fd50cd96/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 33705 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090902/fd50cd96/attachment.jpeg>
More information about the Equest-users
mailing list