[Equest-users] Baseline Airflow Autosizing

Matutinovic, Luka LMatutinovic at halsall.com
Mon Oct 26 06:32:31 PDT 2009


Reniel,
 
Are you referring to the sizing runs from G3.1.2.2.1?  If so, leave the
design cfm on each air-handler blank (see screenshot below) and eQuest
will size the flows based on the sizing option you've specified (Click
on a system, go the Basics tab, and see "Sizing Option").  
 
If you need to size the baseline equipment capacity as per G3.1.2.2,
then multiply the auto-sized flows from the first step, by 1.25 for
heating and 1.15 for cooling and enter the result as the design cfm.
 
I think you might be able to do the second step directly by specifying a
sizing ratio (see second screenshot), although for whatever reason I
haven't done it this way in the past, so I'd be curious to hear from the
more experience eQuesters what approach they take.
 
Hope the helps,
 

Luka Matutinovic, B.A.Sc., LEED(r) AP

Green Building Consultant
 
T. 416.644.0649

F. 416.487.9766  
Toll Free 1.888.425.7255
www.halsall.com 

HALSALL ASSOCIATES LTD. 
Toronto  Richmond Hill  Ottawa  Sudbury 
Burlington  Calgary  Vancouver  Dubai 

'50 Best Workplaces in Canada' 
2009 Globe and Mail
P Please consider the environment before printing this e-mail

 
 
 
 
 
 
 

________________________________

From: reniel barroso [mailto:renielbarroso at yahoo.com] 
Sent: Sunday, October 25, 2009 1:37 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Baseline Airflow Autosizing


 
I've been trying to look on the equest interface where we can set the
airflow to autosize itself as per LEED baseline requirement.
I don't think we have this option here. Have we?
 
Thanks in advance.
 
Reniel


 

________________________________

New Email names for you!
<http://sg.rd.yahoo.com/aa/mail/domainchoice/mail/signature/*http://mail
.promotions.yahoo.com/newdomains/aa/> 
Get the Email name you've always wanted on the new @ymail and
@rocketmail.
Hurry before someone else does!
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20091026/56553b2f/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 86545 bytes
Desc: Outlook.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20091026/56553b2f/attachment.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 106222 bytes
Desc: Outlook.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20091026/56553b2f/attachment-0001.jpeg>


More information about the Equest-users mailing list