[Equest-users] PHOTOCELL-CTRL problem
Nick Caton
ncaton at smithboucher.com
Fri Oct 23 12:11:42 PDT 2009
I'm at the point of troubleshooting the application of PHOTOCELL-CTRL to
my exterior lighting loads.
My lighting loads are accounted under an electrical meter as shown on
the attached image.
The help file and previous discussions on this mailing list seem to
indicate that the use of PHOTOCELL-CTRL requires that the referenced
schedule be of the type "ON/OFF."
The conflict is that a schedule applied to an exterior direct load under
an electrical meter must be of the type "MULTIPLIER." If I set up my
schedules as "ON/OFF" per the PHOTOCELL-CTRL directions, they don't
appear in the dropdown list to be selected in the attached screengrab.
I want to apply PHOTOCELL-CTRL behavior for my exterior light
schedules... can anyone point me in the right direction to make this
happen? Is it possible PHOTOCELL-CTRL just works when the schedule is
of the type "MULTIPLIER?"
Attached is the the DOE2 help file entry in its entirety for reference.
Also for reference, my 3 Exterior Lighting Schedules look like this at
the moment:
----------DAY
"ExtLtg Dusk/Dawn DaySch" = DAY-SCHEDULE-PD
TYPE = ON/OFF
VALUES = ( 1, 1, 1, 1, 1, 1,
1, 1, 1, 1, 1, 1,
1, 1, 1, 1, 1, 1,
1, 1, 1, 1, 1, 1 )
..
"ExtLtg Dusk/12AM DaySch" = DAY-SCHEDULE-PD
TYPE = ON/OFF
VALUES = ( 0, 0, 0, 0, 0, 0,
0, 0, 1, 1, 1, 1,
1, 1, 1, 1, 1, 1,
1, 1, 1, 1, 1, 1 )
..
"ExtLtg Security DaySch" = DAY-SCHEDULE-PD
TYPE = ON/OFF
VALUES = ( 0, 0, 0, 0, 0, 0,
0, 0, 0, 0, 0, 0,
1, 0, 0, 0, 0, 0,
0, 0, 0, 0, 0, 0, )
..
----------WEEK
"ExtLtg Dusk/Dawn WeekSch" = WEEK-SCHEDULE-PD
TYPE = ON/OFF
DAY-SCHEDULES = ( "ExtLtg Dusk/Dawn DaySch" )
..
"ExtLtg Dusk/12AM WeekSch" = WEEK-SCHEDULE-PD
TYPE = ON/OFF
DAY-SCHEDULES = ( "ExtLtg Dusk/12AM DaySch" )
..
"ExtLtg Security WeekSch" = WEEK-SCHEDULE-PD
TYPE = ON/OFF
DAY-SCHEDULES = ( "ExtLtg Security DaySch" )
..
----------ANNUAL
"ExtLtg Dusk/Dawn AnnSch" = SCHEDULE-PD
TYPE = ON/OFF
PHOTOCELL-CTRL = DAY-OFF
MONTH = ( 12 )
DAY = ( 31 )
WEEK-SCHEDULES = ( "ExtLtg Dusk/Dawn WeekSch" )
..
"ExtLtg Dusk/12AM AnnSch" = SCHEDULE-PD
TYPE = ON/OFF
PHOTOCELL-CTRL = DAY-OFF
MONTH = ( 12 )
DAY = ( 31 )
WEEK-SCHEDULES = ( "ExtLtg Dusk/12AM WeekSch" )
..
"ExtLtg Security AnnSch" = SCHEDULE-PD
TYPE = ON/OFF
MONTH = ( 12 )
DAY = ( 31 )
WEEK-SCHEDULES = ( "ExtLtg Security WeekSch" )
NICK CATON, E.I.T.
PROJECT ENGINEER
25501 west valley parkway
olathe ks 66061
direct 913 344.0036
fax 913 345.0617
Check out our new web-site @ www.smithboucher.com
From: Brian Fountain [mailto:bfountain at greensim.com]
Sent: Friday, July 10, 2009 9:12 PM
To: Nick Caton
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Editing External lighting Schedule
You mean something like this (from the new features help file)...
PHOTOCELL-CTRL
Accepts a code-word specifying whether the hourly value in the
referenced DAY-SCHEDULE can be overridden either ON (value = 1.0) or OFF
( value = 0.0) according to whether it is day or night.
DAY-OFF Forces the hourly schedule value to be 0.0
whenever the sun is up.
DAY-ON Forces the hourly schedule value to be 1.0
whenever the sun is up.
NIGHT-OFF Forces the hourly schedule value to be 0.0
whenver the sun is down.
NIGHT-ON Forces the hourly schedule value to be 1.0
whenever the sun is down.
For example, assume lighting in a parking lot is to be on from dusk
until 11 p.m. The earliest the lights are allowed to illuminate is 4
p.m., but will not actually start until the sun is down:
"Parking Lot DSch" = DAY-SCHEDULE-PD
TYPE = ON/OFF
VALUES = ( 0., 0., 0., 0., 0., 0.,
0., 0., 0., 0., 0., 0.,
0., 0., 0., 1., 1., 1.,
1., 1., 1., 1., 1., 0. )
"Parking Lot WSch" = WEEK-SCHEDULE-PD
TYPE = ON/OFF
DAY-SCHEDULES = ("Parking Lot DSch")
..
"Parking Lot Sch" = SCHEDULE-PD
TYPE = ON/OFF
PHOTOCELL-CTRL = DAY-OFF
MONTH = (12)
DAY = (31)
WEEK-SCHEDULES = ("Parking Lot WSch")
..
Nick Caton wrote:
With regard to exterior lighting, It occurred to me today that eQuest
currently has the capability to determine the operating hours of
interior lights based on an amount of daylight, specific to the hours of
daylight occurring during the year for a given location, using the
daylighting functions...
How much of a stretch/challenge would it be to accurately determine how
often photocell-controlled exterior lights are operating through the
year based on available daylight outside of the building??
It might be an awesome feature to consider for future wizards: where one
simply defines the exterior lighting wattage, and could additionally
designates realistic timeclock/photocell controls, such as "on when it
turns dark and off after 2AM."
NICK CATON, E.I.T.
PROJECT ENGINEER
25501 west valley parkway
olathe ks 66061
direct 913 344.0036
fax 913 345.0617
Check out our new web-site @ www.smithboucher.com
-----Original Message-----
From: equest-users-bounces at lists.onebuilding.org [
mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of
Matutinovic, Luka
Sent: Friday, July 10, 2009 9:03 AM
To: John Aulbach; equest-users at lists.onebuilding.org; nate murray
Subject: Re: [Equest-users] Editing External lighting Schedule
I had limited success in editing the Wizard schedules by adjusting the
max and min thresholds on the vertical axis and the start and end hours
along the top axis. My understanding is that eQuest generates those
schedules based on the building type definition at the beginning of the
shell wizard. I had many headaches trying to edit the schedule after I
realized I selected the wrong building type, especially when dealing
with multiple shells. I inevitably end up using John's approach once in
the detailed mode.
When people are creating models for LEED, do you use the schedules found
in the back of the 90.1 User's Manual, or do you create your own
schedules? How has the USGBC reviewed this issue since according to App
G, schedule creation is up to the designer and the "rating authority"?
It would seem to me that the USGBC wouldn't care as long as you use
schedules that are reasonable for the building type and anticipated
operation, and that the reference building uses the same ones (unless
daylight controls or demand controlled ventilation is being dealt with
through schedules and not simulation software directly).
Any thoughts?
Thanks,
Luka Matutinovic
-----Original Message-----
From: equest-users-bounces at lists.onebuilding.org [
mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of John
Aulbach
Sent: Friday, July 10, 2009 1:47 AM
To: equest-users at lists.onebuilding.org; nate murray
Subject: Re: [Equest-users] Editing External lighting Schedule
Nate:
The only way I know to edit such schedules is to change the mode to
Detailed Edit, then make the schedule changes.
If you try to go back to the Wizard mode, those changes will be deleted.
John Aulbach
--- On Thu, 7/9/09, nate murray <natemurr at gmail.com>
<mailto:natemurr at gmail.com> wrote:
From: nate murray <natemurr at gmail.com>
<mailto:natemurr at gmail.com>
Subject: [Equest-users] Editing External lighting Schedule
To: equest-users at lists.onebuilding.org
Date: Thursday, July 9, 2009, 5:59 PM
Hi,
I want to make the external lighting schedule so that there is a
little bit smaller loads in april and october then the rest of
the
months. I see the monthly profiles on the External lighting
screen in
Design Wizard, but how do I go about editing those monthly
profiles...if that's what I should do.
Thanks,
--
Nathan Murray
-----Inline Attachment Follows-----
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20091023/6b0ab9dc/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20091023/6b0ab9dc/attachment.jpeg>
-------------- next part --------------
An embedded and charset-unspecified text was scrubbed...
Name: PHOTOCELL-CTRL help.txt
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20091023/6b0ab9dc/attachment.txt>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: exterior lighting loads entry.GIF
Type: image/gif
Size: 27918 bytes
Desc: exterior lighting loads entry.GIF
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20091023/6b0ab9dc/attachment.gif>
More information about the Equest-users
mailing list