[Equest-users] Huge PV array... can't model enough panels
    Heather.Hardie-Hill at CH2M.com 
    Heather.Hardie-Hill at CH2M.com
       
    Tue Oct  6 16:16:50 PDT 2009
    
    
  
I'm trying to model a PV array on a gigantic roof.
According to the criteria for MODULES-SERIES I should calculate the number of panels in my array by diving the max tracking voltage for the inverter by the max power voltage per panel
(in my case this is 600/78.3 = 7.66 = 7)
Additionally the criteria for MODULES-PARALLEL says that I should multiply the inverter capacity by the number of inverters, divided by the module capacity at the maximum power point, divided again by the number of modules in series.
(in my case this is (500kW*4)/(78.3V*2.55A/1000W/kW)/7 = 1430.9 = 1430) Unfortunately I cannot enter anything above 1000... any suggestions?
Thanks!
Heather Hardie-Hill
EIT, LEEDTM AP
Advanced Design and Simulation
CH2M HILL
Industrial & Advanced Technologies
2020 SW Fourth Ave
Portland, OR 97201
ph: (503).872.4509
e: heather.hardie-hill at ch2m.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20091006/6010a1b5/attachment.htm>
    
    
More information about the Equest-users
mailing list