[Equest-users] Equest Base Model vs. ASHRAE 90.1
Nick Caton
ncaton at smithboucher.com
Tue Nov 24 08:20:17 PST 2009
John,
At the moment, it's up to the end-user to be sure your baseline model is
meeting the 90.1 minimum baseline criteria. If you haven't already
checked it out, Appendix G explains how the model is to be set up and
calibrated to a level of performance (measured via unmet load hours)
that's to be in the same ballpark as your proposed design. If you apply
all design criteria there into eQuest, then you're following 90.1.
I think you're describing and hoping to find eQuest can behave similarly
to COMcheck and other "plug and chug" type compliance documentation
software. I had the same hopes when I first got into the program...
Over time though I've come to understand that 90.1 has so many
gray/interpretable areas that I'm not sure that a "push-button baseline
builder" is really a desirable thing for the task of energy modeling.
Until the day comes when software developers are producing "intelligent"
energy modeling software that makes evaluative decisions as effectively
as a human being, I don't think the task of "generate a baseline energy
model per 90.1" is even a feasible concept. Even if such a (complex)
feature was around to use, you'd still have to do a complete proposed
model for the baseline to reference for
geometries/occupancies/zoning/etc - building the baseline after that is
not a huge relative investment of time in my experience...
In summary, I don't think effective/useful energy modeling for
90.1-based compliance is conceptually possible without involvement from
a human that's at least somewhat familiar with 90.1's Appendix G - it
cannot be automated without a degree of accuracy loss that I think most
would find unacceptable.
That's not to say the process couldn't be made easier with eQuest
(following is a suggestion with that in mind), and I understand other
"for-cost" energy modeling software do generate compliance certificates
of sorts for baseline/proposed LEED comparisons (or at least the LEED
template would lead me to believe this). My impression however is that
where the current evolution of eQuest can fall behind it's "competition"
in cases regarding user-interface (though it's definitely better than a
lot of what's out there), it excels in breadth and depth of modeling
energy behaviors, and in a less measureable way because of the massive
community of professional energy modelers embracing and offering each
other support for the program through forums like this one. And of
course, you can't beat free =).
For the record, I do think a good "wishlist" item for the coming
versions of eQuest, to facilitate easier, more consistent and less
error-prone 90.1 baseline modeling for users of all experience levels,
would be to create a library of 8 systems for use during HVAC system
wizard-level definition (See attached screenshot/paint masterpiece for
when/where/what I'm thinking). These would define a set of defaults for
one of the 8 standard baseline systems, but would still require the
end-user to determine project specific wizard-level criteria (such as
climate zone-specific economizer/high limit requirements and such).
I've noted that the recent 90.1-2007 and 90.1-2004 are identical in
these definitions, so that lends some consolation that such efforts
would not become "out-of-date" for some time to come.
One last note: do be sure you're using the latest version (3.63b)... I'm
observing after clicking 'Help' -> 'About eQUEST...' my installation of
3.63b contains the line "eQUEST, version 3.63, build 6510," if that
helps you to verify.
Apologies for the wall of text - it's a recurring habit of mine...
~Nick
NICK CATON, E.I.T.
PROJECT ENGINEER
25501 west valley parkway
olathe ks 66061
direct 913 344.0036
fax 913 345.0617
Check out our new web-site @ www.smithboucher.com
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of John
Wearstler
Sent: Tuesday, November 24, 2009 7:24 AM
To: Equest Forum
Subject: [Equest-users] Equest Base Model vs. ASHRAE 90.1
Hello All,
I am fairly new to using Equest. (version 3.63). In a 12 page overview,
it indicates that future enhancements to Equest will include building
energy code compliance checking, initially: California Title 24 and
later, ASHRAE 90-1. When modeling the base building for comparisons, I
think the goal would be to enter data that allows the base to just pass
the 90-1 criteria, such as a minimum btuh/ square foot efficiency. This
would permit the greatest difference to be shown in a comparison.
How does Equest control the base model to meet this 90-1 minimum? Is
there a built-in data checking/ evaluation/ editing mechanism or is it
up to the user to enter the exact minimum value data to show the base
model just meeting 90-1? Are certain parts of the Equest program
calculating mechanism following 90-1?
Thank you in advance,
--
John Wearstler
Senior Designer
Larsen Engineering, Inc.
4662 Larwell Drive
Columbus, Ohio 43220
614-459-4002 (voice)
614-459-3124 (fax)
jwearstler at larseneng.com (e-mail)
This transmission may contain information that is privileged,
confidential, or exempt from disclosure under applicable law. If you
are not the intended recipient, you are hereby notified that any
disclosure, copying, distribution, or use of the information contained
herein is strictly prohibited. If you received this transmission in
error, please contact the sender and destroy the material in its
entirety.
Email transmission cannot be guaranteed secure or error-free. Computer
viruses can be transmitted via email - check email and any attachments
for viruses. Larsen Engineering Inc. does not accept liability for
errors or omissions resulting from transmission or any damage caused by
a virus transmitted by this email.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20091124/550484e3/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20091124/550484e3/attachment.jpeg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: 90,1 baseline idea.PNG
Type: image/png
Size: 41805 bytes
Desc: 90,1 baseline idea.PNG
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20091124/550484e3/attachment.png>
More information about the Equest-users
mailing list