[Equest-users] Zone Reheat Delta-T
Dennis Hunt
dhunt at summitbe.com
Thu Nov 19 10:02:28 PST 2009
Thanks Bill, RB for your input,
I looked at the BEPS and found Heating, cooling, Vent Fans, Pump&Aux all
went up for the 20F Zone Reheat Delta-T.
Hours coincident Cool-Heat Load and Fan electric During Heat & Cool jumped
significantly. Any thoughts on this?
No unmet hours for either case
Thanks,
Dennis
-----Original Message-----
From: Bishop, Bill [mailto:wbishop at pathfinder-ea.com]
Sent: Thursday, November 19, 2009 5:30 AM
To: R B; Dennis Hunt
Cc: equest-users at lists.onebuilding.org
Subject: RE: [Equest-users] Zone Reheat Delta-T
Dennis,
The first thing you should look at anytime you are analyzing the
difference in energy use is your BEPS/BEPU reports. Is the difference in
heating, cooling, fan energy, pumping? As R B said, is there a
difference in unmet hours?
For VAV-specific design/energy issues, check out this free resource:
http://www.energydesignresources.com/Technology/HVACDesign/tabid/97/arti
cleType/ArticleView/articleId/331/Default.aspx
Regards,
Bill
William Bishop, EIT, LEED(r) AP | Pathfinder Engineers LLP
Mechanical Engineer
134 South Fitzhugh Street
Rochester, NY 14608
T: (585) 325-6004 Ext. 114
F: (585) 325-6005
bbishop at pathfinderengineers.com
www.pathfinderengineers.com
P Please strive to live sustainably.
-----Original Message-----
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of R B
Sent: Thursday, November 19, 2009 7:59 AM
To: Dennis Hunt
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Zone Reheat Delta-T
one think I can think of is - there might be more unmet heating hours
in the first case.
On 11/18/09, Dennis Hunt <dhunt at summitbe.com> wrote:
> eQUEST users,
>
>
>
> I am modeling a simple 9 story office building in v3.63. The system
type is
> VAV w/ HW Reheat. One Fan system per floor.
>
> With a 20F Zone Reheat Delta-T the Annual Energy Consumption is 38%
higher
> than it is with a 30F Zone Reheat Delta-T.
>
>
>
> This is not intuitive to me why the energy use greatly increases with
a
> lower zone reheat Delta-T.
>
>
>
> Thanks for any help,
>
>
>
> Dennis Hunt
>
> Summit Building Engineering
>
> dhunt at summitbe.com
>
>
>
>
>
>
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20091119/8405766d/attachment.htm>
More information about the Equest-users
mailing list