[Equest-users] Simple question...hopefully

Vikram Sami VSami at lasarchitect.com
Mon Nov 16 14:52:37 PST 2009


There was a paper written by Victor Olgyay & Myself (published at the
ASES 2006 conference in Denver I think) where we looked at optimizing
glazing with two case studies in different climatic conditions - Atlanta
& Hawaii. We separated out the three properties - U-Value, SHGC & Tviz.
The Hawaii building actually performed better with the single glazed
units, whereas Atlanta with a significant winter season was more
intuitive - performing better with the lower U-Values. The other factor
is balance point temperature - if you have a really high internal heat
load, sometimes the higher U-Value might be beneficial even in cooler
climates. 

 

 

SHGC & T-Viz need to be examined in concert with each other. There are
high performance systems that get you the best of both worlds - Solarban
70 on Starphire glass is one of them. 

Vikram Sami, LEED AP 
Direct Phone 404-253-1466 | Direct Fax 404-253-1366 

LORD, AECK & SARGENT ARCHITECTURE



 

From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Kevin
Kyte
Sent: Monday, November 16, 2009 3:46 PM
To: Nick Caton; David Delasantos; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Simple question...hopefully

 

Increased glazing performance may result in less thermal transfer
through the envelope.  This may result in increased or deceased energy
savings.  Depending on climate, varying heat transfer through
fenestration may result in more energy use in the winter and less in the
summer or vice versa.  There is usually a happen middle point which will
give the best returns.  The same applies to increasing and decreasing
insulation.

 

________________________________

From: Nick Caton [mailto:ncaton at smithboucher.com] 
Sent: Monday, November 16, 2009 12:21 PM
To: David Delasantos; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Simple question...hopefully

 

In a recent project,  our architect decided to "upgrade" to nicer (more
expensive) glass.  These fenestrations had marginally better thermal
properties, so I had the same surprise to find the annual energy figures
going UP...

 

After some investigation, it turned into an important design lesson
which may or may not apply to your case:   This project had a
significant amount of daylighting, and the "improved" glass had a
significantly lower Tvis figure.  Less light in means more energy spent
on the lighting system!

 

In the role of lighting system designer, I used to ignore things like
glass transmissivity, as I was taught to design around the worst case
(i.e. nighttime where window contributions have little/no effect)... now
I pay very close attention when daylight harvesting is a part of the
project!

 

Hope this helps either your current situation, or otherwise in the
future!

 

~Nick

 

 

 

NICK CATON, E.I.T.

PROJECT ENGINEER

25501 west valley parkway

olathe ks 66061

direct 913 344.0036

fax 913 345.0617

Check out our new web-site @ www.smithboucher.com 

 

From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of David
Delasantos
Sent: Monday, November 16, 2009 11:02 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Simple question...hopefully

 

I ran a very quick and dirty EEM to compare the effects of using a
different glass type when compared to the baseline model, which was
created in the SD Wizard.  Contrary to my expectations, the higher
performance glass resulted in higher annual energy usage!  The glazing
is the only component I changed in the model.  If anyone can speak to
this result, I would appreciate it.

Thank you...DD 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20091116/cb8646e6/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1459 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20091116/cb8646e6/attachment.jpeg>


More information about the Equest-users mailing list