In order to change the zoning between floors, each floor would be a shell
so you need to use the DD wizard to create your model.

For the attrium, create that zone in both shells, then in the detailed
interface, create an air-wall between the two vertical zones.

The multi-level option only works within a given shell.



> Hello All,
>
> I'm modeling a two floor building with very different usage (first floor,
> mostly kitchen, dining area and rest rooms; second floor has mostly
> offices and conference rooms). So, zoning for HVAC would be quite
> different for both the floors. Is there a way I can model the building as
> a single shell with different zoning for the floors? Or, do I have to
> model each floor as an individual shell?
>
> Also, along the south wall there is an "atrium" with a 'gallery' in the
> second floor from which one can look down into the first! How exactly do I
> model that? I can go to zoning characteristics and select that zone to be
> a multi-level atrium, but what do I do when I define second floor?
>
> I would greatly appreciate if you can help me answer these Questions.
> Thank you in advance.
> -Anand
>