[Equest-users] eQuest -Warning :SPACE EL1 Core Spc (G.C39) has 0 delayed walls, 1 delayed floors

Jon Evans JEvans at sustaineng.com
Wed Jun 17 07:26:39 PDT 2009


Kathiresan,

Ashu's approach eliminates the warning.

But, the reason the warning occurs is overriding the layers input for walls, roof, floor to be a U-value override (user input). The layers input accounts for the time delay properties of the wall (think of it like a capacitor) while the U-value override only looks at the steady state heat transfer.

Thanks.


Jon Evans, PE, LEED AP



Sustainable Engineering Group LLC

431 Charmany Drive Suite 102

Madison, WI 53719



Tel: (608) 231 9664 x 13

Fax: (608) 231 9665

E-mail: jevans at sustaineng.com

Web: www.sustaineng.com

________________________________
From: ashu gupta [mailto:kce2 at kamalcogentenergy.com]
Sent: Wednesday, June 17, 2009 12:50 AM
To: cic at jci.com
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] eQuest -Warning :SPACE EL1 Core Spc (G.C39) has 0 delayed walls, 1 delayed floors and 0 delayed ceilings

Hi Kathiresan,

To eliminate this warning you have to double click on this space and go to the content option then fill the minimum floor weight =70lb/ft².

Window for your reference

[cid:image001.jpg at 01C9EF2D.B7EF4D50]


Thanks

Ashu Gupta,
Project Engineer,
Kamal Cogent Energy,


________________________________
From: equest-users-bounces at lists.onebuilding.org [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of cic at jci.com
Sent: Wednesday, June 17, 2009 10:37 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] eQuest -Warning :SPACE EL1 Core Spc (G.C39) has 0 delayed walls, 1 delayed floors and 0 delayed ceilings


Dear All.

I am getting the following warning while running equest, What needs to be done to eliminate this error in the model?.

SPACE EL1 Core Spc (G.C39) has 0 delayed walls, 1 delayed floors and 0 delayed ceilings. There should be at least a delayed wall and floor, a delayed wall and ceiling, or a delayed ceiling and floor for custom weighting factors to be calculated. ASHRAE weighting factors with floor weight of 70 lb/ft2 (342 kg/m2) will be used for this space. (lLineNum = 1000000)
Line  7871:  Warning Encountered:

Advance thanks for the help.

Regards,
Kathiresan
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090617/062d4fc3/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 49262 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090617/062d4fc3/attachment.jpg>


More information about the Equest-users mailing list