Right click on the two parameters to the right (Static & Total Eff) and
select 'Restore to Default'.  When those numbers are input it locks out
the kW/CFM input.

 

Robby Oylear, LEEDR AP

Mechanical Engineer

direct: 206.788.4571

cell: 206.354.2721

www. <http://www.rushingco.com/> rushingco.com

 

From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Josh
Doherty
Sent: Thursday, June 04, 2009 2:17 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Fan Design kW/CFM

 

Hi-

In ASHRAE 90.1-2004 they specify a design kW/CFM that I need to model for
my LEED baseline building.  In eQuest I see there is an input for this
item.but I can not figure out how to edit the value?  Does anybody know
how I can specify the kW/CFM as opposed to the static in. Wg for the Fan
Power Parameters?  Thank you all for your help!

 

 



 