[Equest-users] [Bldg-sim] loop to loop heatpump in equest
    Nick Caton 
    ncaton at smithboucher.com
       
    Fri Jul 24 11:09:15 PDT 2009
    
    
  
I've chatted with Rashmi and feel like others may want to know how this
can be done in the future...  Also copying [Equest-users] on this
discussion as advised by a list administrator.  
 
 
See attached screengrab for a simple visual of how I accomplished
this...
 
Setting up the 4-pipe system sourced from a closed ground loop:
1.	Create a 'chiller' of the type 'water-to-water heat pump'
2.	Create an independent circulation loop of the type 'lake/well'
3.	Create a ground loop heat exchanger of the type 'lake/well'
4.	Select as the chiller CW loop and GLHX circulation loop the
independent loop you created - they should connect without errors
5.	Assign a custom temperature schedule for the lake/well ground
loop in the screen that pops up when you double click the GLHX (read on)
6.	Make sure the default head/pump properties for the circulation
loop and GLHX make sense for your system - adjust as necessary.  (i.e.
if it's a closed ground loop, there shouldn't be static head)
 
The tricky thing is that both Rashmi and I were dealing with closed-loop
ground heat exchanger (not lake/well).  The solution I came to model
this was to temporarily save the project in a separate directory to keep
my work, then go back to the wizards and heat/cool the same building
reasonably using the DX/DX heating/cooling ground source heatpump
option, with all appropriate ground and field properties well defined.  
 
Once this is done, you can have eQuest additionally generate an hourly
report over of the resulting ground loop temperatures throughout the
year (actual procedure eludes my memory, but it's in the archives).
Once this is done, I used that raw data to come up with the resulting
weekly average temperatures in the ground loop using excel.  I then used
these figures to create a custom temperature schedule for the actual
project, which was assigned to the GLHX as mentioned above.  This way
you're reasonably accurately representing what temperatures the
water-to-water equipment is seeing coming out of the ground throughout
the year based on your actual geographic, ground loop, and soil
condition variables as defined.
 
The final logical step, and one I'm currently working on learning for
myself, is defining a custom performance curve for the water-to-water
equipment that's representative of the real thing.  I have been advised
the default chiller curves as well as the water-to-air heatpump curves
from the Climatemaster eQuest add-on are not appropriate for modeling
water-to-water heatpumps. 
 
Best of luck!
 
PS: Apologies for the screenshot's quality - I had issues making it
small enough for the mailing list to accept.
 
NICK CATON, E.I.T.
PROJECT ENGINEER
25501 west valley parkway
olathe ks 66061
direct 913 344.0036
fax 913 345.0617
Check out our new web-site @ www.smithboucher.com 
 
________________________________
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Anthony
Hardman
Sent: Friday, July 24, 2009 10:13 AM
To: 'Rashmi Sonal'; bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] loop to loop heatpump in equest
 
Would the following get you close enough (ignoring the DOAS side)?
 
1)      Specify a water-air HP system
2)      Zero out the fan energy
3)      Factor the load side pumping energy into the EIR of the HP
a.       Alternatively, you could add your load side pump energy to the
source side pump
 
Obviously there's limitations either way and I've never tried this, just
thinking out loud.  Certainly someone else out there can comment who has
attempted this?
 
Anthony Hardman
Mechanical Engineer
Geo-Energy Services
 
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Rashmi
Sonal
Sent: Thursday, July 23, 2009 3:39 PM
To: bldg-sim at lists.onebuilding.org
Subject: [Bldg-sim] loop to loop heatpump in equest
 
Hi All, 
 
I am trying to model a building with water-to-water heat pump connected
to ground HX and 4-pipe AHUs with induction unit at the terminal. 
I have specified induction unit at the terminal, to model active chilled
beams, with a dedicated outdoor air unit. But with this configuration on
airside I am not able to attach the water to water heat pump to any
condenser water loop on the water side. Is there a way I can model GSHP
serving active chilled beams in equest?
 
Thanks in advance. 
 
Rashmi Sonal, LEED AP
Environmental Designer
Computational and Simulation Analysis (CoSA)
www.burohappold.com
Tel: (+1) 212 616 0285
This transmission is confidential and intended solely for the person or
organization to whom it is correctly addressed. If you are not the
intended recipient of this transmission, you should not take any action
in reliance on it. Further, this transmission may contain confidential
design and other information owned by Buro Happold Consulting Engineers
PC. You should not copy, distribute, use, offer for sale or hire such
information or in any way infringe the design and intellectual property
rights of Buro Happold Consulting Engineers PC. It is intended that
communication by email from Buro Happold Consulting Engineers PC or its
employees is limited to communications connected to the services
provided by Buro Happold Consulting Engineers PC. Buro Happold
Consulting Engineers PC accepts no liability for any communications not
connected to the services it provides. Computer viruses may be
transmitted or downloaded onto your computer system via email
communication. It is the recipient's responsibility to take any action
necessary to prevent computer viruses being transmitted in this way.
Accordingly, Buro Happold Consulting Engineers PC disclaims 
This message has been scanned by MailController
<http://www.mailcontroller.altohiway.com/> .
Click here
<https://www.mailcontroller.altohiway.com/sr/To8sCHyQdZfTndxI!oX7UjKY4eY
AubKEx9b0nNw6fwG1W6Q!6WUsU+sYqtple3ZFLIHnjTmFckyl3fOT1a7RlQ==>  to
report this email as spam.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090724/210f5e63/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: screengrabsmall.JPG
Type: image/jpeg
Size: 142237 bytes
Desc: screengrabsmall.JPG
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090724/210f5e63/attachment.jpeg>
    
    
More information about the Equest-users
mailing list