[Equest-users] Water Side Economizers
B. Fountain
bfountain at greensim.com
Wed Jul 8 10:43:30 PDT 2009
If you are using the newer version of eQUEST (3.62 or 3.63) then the water
side economizer is modelled as a new chiller of type "water economizer".
It models it as a heat exchanger between the condenser loop and the
chilled water loop and automatically runs this "chiller" when ambient
conditions allow. (in contrast to one of my earlier posts which stated
you needed an equipment control -- you don't). There is some requirement
for 1 condenser loop per water side chiller so check the new features
documentation for the water-side economizer chiller.
If you are using the air-side keywords for a water side economizer (the
"old" way), you need to set up a strainer cycle keyword on the cooling
tower and it adds new coils to the air stream (which could cause the
increased fan energy) -- I think -- I haven't done it this way so you'd
really need to check the docs.
I have had what I think is good success using the water side economizer
chiller in 3.63.
Best of luck,
Brian
> I'm trying to model a waterside economizer in eQUEST and I'm getting
> curious results. The building energy usage goes up. There is no real
> change to the space cooling load, but the fan energy doubles and there
> is a 25% increase in pump energy (expected). It looks like it's turning
> on the equipment for the economizer, but its running the chiller as
> well.
>
>
>
> What am I missing here?
>
>
>
> Vikram Sami, LEED AP
> Direct Phone 404-253-1466 | Direct Fax 404-253-1366
>
> LORD, AECK & SARGENT ARCHITECTURE
> 1201 Peachtree Street NE, Suite 300, Atlanta, GA 30361
> Responsive Design * Technological Expertise * Exceptional Service
> Please visit our new website | www.lordaecksargent.com
> <file:///\\www.lordaecksargent.com\>
>
> P Think GREEN before you print.
>
>
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
More information about the Equest-users
mailing list