[Equest-users] Baseline Lighting Power/Schedule
Bishop, Bill
bbishop at PathfinderEngineers.com
Thu Aug 27 11:20:05 PDT 2009
Hi Brett,
I agree with your interpretation (1.), below, for the baseline. Then you
apply the Table G3.2 power adjustment to the proposed building for
spaces that have occupancy sensors, as described in Table G3.1, No
6(g)., using the same lighting schedule as the baseline but with the
as-designed lighting power.
Regards,
William Bishop, EIT, LEED(r) AP | Pathfinder Engineers & Architects LLP
Mechanical Engineer
134 South Fitzhugh Street
Rochester, NY 14608
T: (585) 325-6004 Ext. 114
F: (585) 325-6005
bbishop at pathfinderengineers.com
www.pathfinderengineers.com
P Please strive to live sustainably.
________________________________
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Brett
Fero
Sent: Thursday, August 27, 2009 12:50 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Baseline Lighting Power/Schedule
I would like the opinions of others regarding the interpretation of the
Baseline Building Performance Lighting of Table G3.1 in Appendix G.
Table G3.1, Item 6. Baseline Lighting, last sentence states the
following;
"No automatic lighting controls (e.g. programmable controls or automatic
controls for daylighting utilization) shall be modeled in the baseline
building design, as the lighting schedules used are understood to
reflect the mandatory control requirement in this standard."
I am questioning 2 ways to interpret this in the model. I will use a
10,000 sf office building with typical business hours of operation from
8 am to 6 pm. Most spaces are required to have automatic lighting
controls as specified in the Mandatory Provisions of Section 9.4 (ASHREA
90.1).
1. The Baseline lighting schedule would typically ramp up
starting at maybe 6 am, dip for lunch, and ramp down until maybe 8 pm?
The maximum power density would be that allowed using the space-by-space
method and Table 9.6.1 in ASHRAE 90.1.
2. The Baseline lighting schedule would ramp up starting at maybe
6 am, dip for lunch, and ramp down until maybe 8 pm (typical
scheduling)? The maximum power density would be that allowed using the
space-by-space method and Table 9.6.1 in ASHRAE 90.1. with the 10% Power
Adjustment factor of Table G3.2 applied to the lighting demand of spaces
required to have mandatory controls of Section 9.4.
I have typically used option 1 without question from the USGBC which
increases savings, but was wondering how others have interpreted it.
Are occupancy sensors "programmable controls" - delay time?
Thanks
Brett Fero, P.E., LEED AP
Syracuse, NY 13212
Phone: 315-445-2650
Fax: 315-445-0958
bfero at robsonwoese.com
________________________________
"This message is for the designated recipient only and may contain
privileged, proprietary, or otherwise private information. If you are
not the intended recipient, you are hereby notified that any disclosure,
copying, distribution, or the taking of any action in reliance on the
contents of this information is strictly prohibited. If you have
received this transmission in error, please notify the sender
immediately by e-mail and delete the original message."
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090827/ed3e1bed/attachment.htm>
More information about the Equest-users
mailing list