I am not sure if you have received an answer on this, but it is not that
difficult to create defrost schedules. Basically, start with your daily
schedule for each of your defrosts. The "Schedule Type" for refrigerated
fixtures is "on/off." Then, if you want to defrost 4 x per day, put a
"0" in every hour you do NOT want a defrost. For all hours (4 of them)
you DO want defrosts, put a "1." Then, make your Week and Annual
schedules and have them point to this Day schedule that you just made.
Of course, you will need to fill out the associated Defrost Control
information as well; ie: type, initiation and termination control
methods, and duration.
Best regards,
Christopher Rogers
ENGINEER
DIR 503-961-6191
INTERNAL x361
www.peci.org
<about:../../../../commercial/Current/Marketing/How%20To's/www.peci.org>
Creating the new energy economy
________________________________
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Scott
Lingerfelt
Sent: Tuesday, May 26, 2009 6:00 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Display Case Defrost Schedules
Anyone,
How Do I add a defrost schedule for each of my display cases in the
refrigeration version 3.61? I have equipment added but cannot seem to
get the right schedules for each case! Example: I need to setup 4
defrost/day for my multi-deck dairy. I have looked through the
documentation but it is not straight forward.
Any guidance will be greatly appreciated,
Scott