[Equest-users] pump head
Doug Maddox
DougM at TWGI.com
Mon Aug 24 08:56:06 PDT 2009
Verena,
My understanding is that pump head is the total head seen by the pump,
and it is calculated in the model by summing up the head of the
components of the system (coils, piping, heat exchangers, valves). If
you make an entry for PUMP-HEAD, then that is the design head for the
pump, not necessarily the actual head seen by the pump. If you leave it
blank, the design head will default to the total head of the parts.
The loop head is just the head of the piping, and the command in DOE2 is
actually PIPE-HEAD. I don't think there is a command called LOOP-HEAD.
Doug Maddox
The Weidt Group
dougm at twgi.com
________________________________
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Verena
Kindl
Sent: Monday, August 24, 2009 10:43 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] pump head
Hi,
sorry it is me again, but can anybody explain me the difference between
pump head and loop head? Here in Germany we only have one value for the
complete pressure drop and I do not understand it in the equest help.
Thanks
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090824/6b9419eb/attachment.htm>
More information about the Equest-users
mailing list