[Equest-users] Purchased Heat

YinRic cesseric at hotmail.com
Sun Aug 16 19:32:46 PDT 2009


Hi Dakota,

 

Your information is complete and thorough. Thank you very much!

 

Best Regards,

Rick
 


Subject: RE: [Equest-users] Purchased Heat
Date: Fri, 14 Aug 2009 15:08:54 -0500
From: dakotak at teliospc.com
To: cesseric at hotmail.com
CC: equest-users at lists.onebuilding.org







Rick,
 
I wouldn’t go with no heating; you can model this scenario directly in eQUEST:  
 
·         Make sure you have your steam loop created, then create a steam meter under “Utility & Economics”
·         Assign the meter to your steam loop when prompted
·         Create a utility rate of type “steam” and make sure it is set to serve your steam meter
·         Set up block charges for different times of the year to create your steam rate.  For the three months that have a fixed rate, you could create a block with $0/unit and define a minimum $5,000 charge (steam rate properties…Min/Max Charges tab…Fixed Chrgs ($/mon) column).  Set the min to $0 or whatever it should be for the other 9 months.  Note that for a steam meter, you can define the Btu/billing unit under the steam meter’s Properties/Basic Specifications tab.
 
Creating the rate schedule will be the hardest part, but it’s not that difficult.  The process is also well-documented in Volume 2 of the supporting documentation.  The way I would do it is:
 
·         Create a block schedule of type “flag” – this will define when your various blocks are active/inactive
·         Create your blocks as needed; you’ll only have two if the rest of the year follows a single rate schedule
·         On each block’s Basic Specifications tab, apply the block schedule you created and give each block a flag value
·         If necessary, adjust your block schedule to ensure it corresponds to the flag values you assigned to the blocks (you will probably have thought this out when creating the schedule, however)
 
To ensure you set it up correctly, you can use the ES-E and ES-F reports to inspect your steam rate’s monthly billing.  Feel free to contact me directly if you have more questions about the above.
 
Thanks,
 
                                
                        DAKOTA KELLEY                                                              
                                Project Designer
 
                                Office:      214-744-6199
                                Cell:         214-280-3825
                                Fax:         214-744-0770 
                
http://www.teliospc.com          3535 Travis St. Suite 115 
dakotak at teliospc.com             Dallas, TX 75204 
 
| MEP ENGINEERING · ENERGY MODELING · LEED CONSULTATION · COMMISSIONING |                         
 
 
CONFIDENTIALITY NOTICE: This email is intended only for the use of the individual or entity to which it is addressed, 
And may contain information that is privileged, confidential and exempt from disclosure under applicable law. If you 
are not the intended recipient, please email the sender immediately, and delete this email from all computers.  Any 
distribution or other use is strictly prohibited.  Copyright © 2009 Telios Corporation.
 
 
 
 


From: YinRic [mailto:cesseric at hotmail.com] 
Sent: Friday, August 14, 2009 12:12 AM
To: Equest User
Subject: [Equest-users] Purchased Heat
 
Hi,
 
In a project to go for LEED, in winter, the heat source is steam purchased from public utility company with fixed rate, say, $5,000/month in spite of the real heating demand, how to simulate this in Equest? ASHRAE 90.1-2004 stated that "For systems using purchased hot water or steam, hot water or steam costs shall be based on actual utility rates, and on-site boilers shall not be modeled in the baseline building design." Is it feasible to choose "no heating" in the proposed case and do some simple calculation instead, say, $5,000/month*3 month=$15,000, to generate a result? 
Any comments are welcome. Thanks.
 
Rick, PE, LEED AP
 
 
 



使用新一代 Windows Live Messenger 轻松交流和共享! 立刻下载!
_________________________________________________________________
Messenger安全保护中心,免费修复系统漏洞,保护Messenger安全!
http://im.live.cn/safe/
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090817/db5f417a/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 3170 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090817/db5f417a/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 2327 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090817/db5f417a/attachment.jpg>


More information about the Equest-users mailing list