[Equest-users] Chiller COP in baseline building
Min-Hwan Yang
yangm at kjww.com
Thu Aug 13 11:54:32 PDT 2009
Sam,
I would input 6.1 COP and specified as rated-condition.
Min-Hwan Yang, CEM, LEED AP
Mechanical Engineer | yangm at kjww.com
200 West Jackson Boulevard, Suite 1200 | Chicago, Illinois 60606
312-294-0501 | Direct: 312-356-3750 | Fax: 312-294-0003
www.kjww.com
"One of the Best AEC Firms to Work For"
Building Design + Construction, March 2008
Everyone,
I am having an issue with determining the baseline chiller COP for a large lab building. The proposed design system is two 1600 ton centrifugal machines with 42F CHWT with 12F delta T, 85 ECWT, and 2.5gpm/ton condenser flow rate. Both units are rated at 5.72 COP which is above the minimum efficiency of 5.60 per Table 6.8.1J.
In the baseline, there are 4- 800 ton centrifugal machines and per Appendix G3.1.3.8, the design supply CHWT should be 44F with a 12F delta T. So the question that arises is: what is the efficiency of the baseline machines? If you use standard rating conditions of 44F CHWT,
85 ECWT, and 3.0 gpm/ton condenser flow rate, the minimum COP should be 6.1. If you use the design conditions for the building, it is 5.60.
6.1 versus 5.6 in lab building of >400,000 sq.ft. is a huge difference and could mean the difference between meeting minimum energy cost savings for EA credit 1.
Any thoughts, help, or experience is greatly appreciated.
This message and any attachments contain information intended for a specific party and may include sensitive or confidential material. If you are not the intended recipient, please do not read, copy, use, or disclose to others. Please notify the sender of the delivery error by reply and then permanently delete this message and all attachments.