Seun:
I have done the tried and true "equivalent" method from ASHRAE 90.1, where they give an equivalent stud (metal or wood) with the insulation between the studs and if any is in front (or behind) the studs. Then pick an insulation that fits that criteria.
Otherwise, you would need to do TWO walls..one with the stud and one without..and percentagize (?) them.
I pick Method A.
John Aulbach
--- On Tue, 8/11/09, Seun Odukomaiya <sodukomaiya at laceindy.com> wrote:
> From: Seun Odukomaiya <sodukomaiya at laceindy.com>
> Subject: [Equest-users] Custom Exterior Walls in eQuest
> To: "equest-users at lists.onebuilding.org" <equest-users at lists.onebuilding.org>
> Date: Tuesday, August 11, 2009, 6:41 AM
>
>
>
>
>
>
>
>
>
>
>
>
>
>
>
> Hi all,
>
> I am modeling a building in eQuest and
> trying to enter a
> custom exterior wall construction in the DD wizard as a
> "Custom,
> Layer-by-Layer Construction". I have been able to add
> most layers but am
> unable to find any wall studs in the library. For example,
> I need to add a
> layer of 6inch wall studs, but there is no such option
> available. In fact, I
> don't see any wall studs available. Has anyone run into
> this issue? How do I
> add studs to my exterior walls. Thank you.
>
>
>
> Seun Odukomaiya, LEED AP -
> Mechanical
> Engineer
>
> L'Acquis
> Consulting Engineers
>
> 280 East 96th Street, Suite
> 280
>
> Indianapolis, IN 46240
>
> voice: (317) 706-2075
>
> fax: (317)
> 706-2076
>
> email: sodukomaiya at laceindy.com
>
>
> web: www.laceindy.com
>
>
> P Please
> consider the environment before printing this
> e-mail.
>
>
>
>
>
>
>
>
>
> -----Inline Attachment Follows-----
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank
> message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
More information about the Equest-users
mailing list