[Equest-users] Equipment Process Loads
David S Eldridge
DSE at grummanbutkus.com
Thu Aug 6 18:58:36 PDT 2009
You might try the compare-it! program to verify the files are identical - sometimes it is difficult to track those down within the interface.
-DSE
Sent from my iPhone
On Aug 6, 2009, at 8:45 PM, "ron lamarre" <lamarre_arch at yahoo.com<mailto:lamarre_arch at yahoo.com>> wrote:
Hi to all:
Our baseline and proposed models have exactly the same misc equipment process loads. The inputs were placed in the detailed interface mode spreadsheet and compared to make sure each space has the correct (and same) W/SF loads.
The PS-E report shows the four baseline exposures with 121560 kWh. The proposed PS-E model report has 121594 kWh. I know this is splitting hairs, but we cannot find any equipment load difference between the two models and we are concerned that LEED will not accept the process loads being different in the Credit Template.
(Note: the large process load is expected with this type of building).
Has anyone encountered this in the past? Thanks for your help.
Ron Lamarre, AIA, NCARB
Architect - LEED AP
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send a blank message to <mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
More information about the Equest-users
mailing list