[Equest-users] No heating?

Kalianda, Angelina Angelina.Kalianda at aecom.com
Thu Apr 23 09:58:48 PDT 2009


95 F & 60 F are the hi/lo temps for off hours/night set back.  I figured
out the problem.  For some reason when I specified hour 1 through 6 and
20 thru 24 to be off in the parametric run, it changes the rest of the
hours to be off as well.  I don't know why it does that because it
doesn't always do that in my other file.  So I have to actually list all
hours, 1 through 24, to be on or off at the respective hours.  

 

Angelina Kalianda, PE, CEM

AECOM Energy

D 858-947-7193

C 760-585-8624

 

________________________________

From: John Aulbach [mailto:jra_sac at yahoo.com] 
Sent: Wednesday, April 22, 2009 9:06 PM
To: equest-users at lists.onebuilding.org; Kalianda, Angelina
Subject: Re: [Equest-users] No heating?

 

Angelina:

 

I am totally confused.

 

The run you sent has a cooling T-stat schedule of 95 DegF, a heating
T-stat schedule of 60, and a fan schedule of always off, unless the
heat/cool limts are exceeded.

 

What am I reading wrong?

 

John Aulbach

--- On Wed, 4/22/09, Kalianda, Angelina <Angelina.Kalianda at aecom.com>
wrote:

	
	From: Kalianda, Angelina <Angelina.Kalianda at aecom.com>
	Subject: [Equest-users] No heating?
	To: equest-users at lists.onebuilding.org
	Date: Wednesday, April 22, 2009, 6:57 PM

	Hi all,

	 

	I'm running a parametric run to change the time schedule from
running 24 hrs to a time schedule (6am to 7pm).  For some reason, it
won't run the heating at all.  When I check the DOE-2 output (PS-H),
heating is zero.  Does anyone have any idea what went wrong?  Attached
is the file.  Thanks all.  

 

 

Angelina Kalianda, PE, CEM

Development Engineer

D 858-947-7193

C 760-585-8624

 

AECOM Energy

440 Stevens Avenue

Suite 250

Solana Beach, CA 92075

T 858-947-7144   F 858-947-7145

www.aecom.com <http://www.aecom.com/> 

 

My e-mail has changed to angelina.kalianda at aecom.com
<http://us.mc01g.mail.yahoo.com/mc/compose?to=angelina.kalianda@aecom.co
m> .  Please update your address books accordingly.

 

* Please consider the environment before printing

 


-----Inline Attachment Follows-----

_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
<http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org>

To unsubscribe from this mailing list send  a blank message to
EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
<http://us.mc01g.mail.yahoo.com/mc/compose?to=EQUEST-USERS-UNSUBSCRIBE@O
NEBUILDING.ORG> 

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090423/34193ed5/attachment.htm>


More information about the Equest-users mailing list