[Equest-users] MZ, heating only
Kalianda, Angelina
Angelina.Kalianda at aecom.com
Thu Apr 16 12:41:24 PDT 2009
Actually I found out it's a Multi-zone heating only system. For
cooling, the campus only uses the outside air. The damper is throttling
between heating deck and OSA deck. I tried using packaged MZ and put
the DX cooling to a separate meter, crankcase heat to 0 kW and
thermostat to restore default but my heating consumption is 3x the
bills. I think because it's heating the supposedly chilled air although
there is no chilled air other than OSA. Any thoughts or ideas?
Angelina Kalianda, PE, CEM
AECOM Energy
D 858-947-7193
C 760-585-8624
________________________________
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Gaurav
Mehta
Sent: Wednesday, April 15, 2009 1:31 PM
To: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] VVT, heating only
Another method:
Don't provide any cooling thermostat schedule to the zone (right click
and select restore default) and set the crankcase heat to 0 kW on
unitary power tab.
Gaurav Mehta, LEED(r) AP
Senior Project Energy Analyst
direct: 206.462.7658
fax: 206.285.7111
www.rushingco.com <http://www.rushingco.com/>
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of
Kalianda, Angelina
Sent: Wednesday, April 15, 2009 12:37
To: Howe, Timothy; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] VVT, heating only
Yes, no cooling and it's HW heating, not furnace. However it has zone
dampers.
Angelina Kalianda, PE, CEM
AECOM Energy
D 858-947-7193
C 760-585-8624
________________________________
From: Howe, Timothy [mailto:Timothy.Howe at stantec.com]
Sent: Wednesday, April 15, 2009 12:24 PM
To: Kalianda, Angelina; equest-users at lists.onebuilding.org
Subject: RE: [Equest-users] VVT, heating only
1. Put the cooling on a separate electric meter so that it does not
report it, or set the cooling thermostat set point to the maximum
allowable value or a combination of these.
2. VVT is an available system type.. not sure if you were asking
because of the no cooling.
3. Utility bill matching is very difficult, you will need to know
more specifics about the schedules of operations, equipment
efficiencies, lighting efficiencies... so on. If it is close +-10% I
would not worry about it, otherwise you will need to massage the model
to fit existing conditions.
Timothy Howe, MS, LEED(r) AP
Mechanical Engineer
Stantec
2060 Brighton-Henrietta Town Line Road
Rochester NY 14623-2792
Ph: (585) 413-5347
Fx: (585) 272-1814
Cell: (585) 330-8681
stantec.com <http://www.stantec.com/>
The content of this email is the confidential property of Stantec and
should not be copied, modified, retransmitted, or used for any purpose
except with Stantec's written authorization. If you are not the intended
recipient, please delete all copies and notify us immediately.
* Please consider the environment before printing this email.
________________________________
From: equest-users-bounces at lists.onebuilding.org
[mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of
Kalianda, Angelina
Sent: Wednesday, April 15, 2009 3:07 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] VVT, heating only
Hi all,
I have a VVT type system but with no cooling, heating only. What kind
of system type I can model that? When I chose the HW furnace with zone
ventilation, the heating consumption was smaller than the utility bill.
If I chose other type of system (package VVT, MZ, etc.), it's assuming
it has some kind of cooling.
Thanks in advance for your help.
Angelina Kalianda, PE, CEM
Development Engineer
D 858-947-7193
C 760-585-8624
AECOM Energy
440 Stevens Avenue
Suite 250
Solana Beach, CA 92075
T 858-947-7144 F 858-947-7145
www.aecom.com <http://www.aecom.com/>
My e-mail has changed to angelina.kalianda at aecom.com
<mailto:angelina.kalianda at aecom.com> . Please update your address books
accordingly.
* Please consider the environment before printing
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090416/35b96feb/attachment.htm>
More information about the Equest-users
mailing list