[Equest-users] Modelling boiler lock out
    John Carpenter 
    jcarpenter at genesysengineering.net
       
    Thu Apr 16 12:12:32 PDT 2009
    
    
  
Angelina,
 
If you are in the detailed edit mode and double click on the hot water loop,
you should see a tab called "operation."
 
If you then change the "Loop operation" to "Snap," the model will allow you
to shut off the boilers at any temperature you wish.  Just make sure you
change the snap location to "outside" instead of a zone.
 
Regards,
 
John Carpenter
Mechanical Engineer
Genesys Engineering
Pelham, NY