Hi Brian,

I would suggest you to refer to the archives of [Equest-users] postings.
Gary Schrader had responded to this query with the following solution:

*You'll need to open your .pd2 file inside of notepad. Search for the text
of the filenames that you have removed, then delete those lines associated
with that(those) file(s) and save.*
* *
*Example:*
* *
*You deleted CAD_1.dwg, but want to keep CAD_2.dwg:*
* *
*<---- Delete everything between these lines ---->*
*CADFile   "CAD - 1"
   FileName = "CAD_1.dwg"
   FilePathOffset = 1
   ScaleUnits = 0
   ScaleValue = 1
   OriginX = 0
   OriginY = 0
   Azimuth = 0
   ..*
*<---- Delete everything between these lines ---->*
* *
*CADFile   "CAD - 2"
   FileName = "CAD_2.dwg"
   FilePathOffset = 1
   ScaleUnits = 0
   ScaleValue = 1
   OriginX = 0
   OriginY = 0
   Azimuth = 0
   ..*
* *
*Hope this helps.*
* *
*Thanks,**
Gary Schrader
Engineer I

TAC
16011 College Blvd, Suite 212
Lenexa, KS  66219

*Hoping that you found a solution!

Regards,
Surabhi Joshi
Student - MS Building Technology
email: surabhi.cca at gmail.com



On Wed, Apr 1, 2009 at 7:02 PM, Brian Trapp <Brian at nkarch.com> wrote:

>  Is there a way to remove the CAD files that have been added to an eQUEST
> project?  I have an eQUEST file that has several CAD files referenced in it,
> and one of them seems to be causing the program to crash.  Changing the CAD
> file paths isn’t working.  I’m new to eQUEST.
>
>
>
> Thank you,
>
>
>
> Brian Trapp, LEED AP
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>


-- 
Surabhi Joshi
Student - MS Building Technology
email: surabhi.cca at gmail.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20090402/09449c11/attachment.htm>


More information about the Equest-users mailing list