[Equest-users] Maximum number of tracked modifications exceeded
Scott Criswell
scott.criswell at doe2.com
Tue Jun 3 22:03:37 PDT 2008
Hi Karen,
I am pretty sure that the "Maximum number of tracked modifications
exceeded" error and simulation abort. Though the error sounds fairly
critical, it is really just an indication that a modification to the
detailed model is causing so many cascading other changes and
re-defaulting that the expression dependency and evaluation mechanism is
unable to keep track of the history of those changes in memory. All
cascading changes however ARE evaluated and posted to BDL (despite this
error message) and we have seen no cases where this error was an
indication that the detailed model was in fact corrupt in some way.
If your model still aborts part way through the simulation, then I
recommend you search through the .SIM output file for any occurrences of
"ERROR" or to the end of the file which may provide an indication of why
the simulation terminated. If this doesn't lead to a solution, then
feel free to forward me your project files (.pd2 & .inp compressed into
a ZIP file) and I will take a look.
- Scott
Karen Walkerman wrote:
> Hi,
>
> I just got a strange error that I have not seen before, nor can I find
> any explanation as to what it means. When I change some entries for
> the System type, specifically those that are required after a previous
> entry (for example, ERV type after indicating that
> "RECOVER-EXHAUST=YES"I get a "Maximum number of tracked modifications
> exceeded" error. And, when I run the model, it freezes at 51%
> complete (June 17). I saw a post with a question from February
> regarding this error, but no responses. Can anyone enlighten me? I
> am not convinced that the error and the simulation quitting are
> related, especially as I changed the System type, and still get the
> error, but the simulation is now running.
>
> Thanks,
>
> --
> Karen
> ------------------------------------------------------------------------
>