You should read the notes at the bottom of the .stat files:

- **Note that the ASHRAE classification shown here is derived algorithmically from the source weather data.
 -   It may not be indicative of the long term climate for this location.


Use the information in  ASHRAE Standard 169 (or 90.1) to define the climate zone -- from the long-term statistics, not a 'typical' weather file.


-----Original Message-----
From: bldg-sim-bounces at lists.onebuilding.org [mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of elenisoulti at co2engineering.eu
Sent: Monday, December 03, 2012 5:12 PM
To: bldg-sim at lists.onebuilding.org
Subject: Re: [Bldg-sim] Bldg-sim Digest, Vol 60, Issue 21

When you open one of the weather files (found in EERE website) as text, you can see the information on the ASHRAE climate zone. I don't think there is a bug in eQUEST since the climate zone definition doesn't depend on the software used for the simulation.

However, the description of the climate zone according to this doesn't seem to agree with calculations based on different data. So I am wondering, since I am using the EERE weather file for my eQUEST simulation for LEED, if I have to define the climate zone as found in the file or as calculated. I hope this makes sense and answers your question.

Thanks,

Eleni
--
Eleni Soulti

On behalf of

CO2 Engineering

Oficina Sevilla

Cartuja - Edificio Marie Curie

C/Leonardo da Vinci 18, Planta1 3ºB

41092 Sevilla | España

T.             (0034) 679883055  
begin_of_the_skype_highlighting            (0034)
679883055      end_of_the_skype_highlighting

London Office

17, Bishops Close

E17 9RP London | UK

T.             (0044) 7969235926  
begin_of_the_skype_highlighting            (0044)
7969235926      end_of_the_skype_highlighting

Oficina Huelva.

Plaza Hermanos Costalero nº 2, 6º A

21001 Huelva | España

T.             (0034) 647143558  
begin_of_the_skype_highlighting            (0034)
647143558      end_of_the_skype_highlighting

w.   www.co2engineering.eu

e.   elenisoulti at co2engineering.eu


Quoting Joe Huang <yjhuang at whiteboxtechnologies.com>:

> I'm confused by both the original post and the subsequent replies.  
> What does this have to do with weather data  or with eQUEST?
>
> Weather files do not list the ASHRAE climate region.  If you got a 
> weather file from the EERE site,  then that's an EnergyPlus EPW 
> weather file.  The ASHRAE Climate Zone shown on an EPW STAT file is 
> calculated by the EnergyPlus weather processor in converting the 
> source weather file into an EPW.  It has no bearing on the weather 
> file itself.  If you think that the Climate Zone is in error, that 
> only means the algorithm used by the EnergyPlus weather processor to 
> calculate the ASHRAE Climate Zone may be faulty for international 
> locations.
>
> Referring to this as a bug in eQUEST, or suggesting the problem might 
> be the eQUEST *.BIN weather file are further off the mark.
>
> Joe
>
> Joe Huang
> White Box Technologies, Inc.
> 346 Rheem Blvd., Suite 108D
> Moraga CA 94556
> yjhuang at whiteboxtechnologies.com
> www.whiteboxtechnologies.com
> (o) (925)388-0265
> begin_of_the_skype_highlighting      &nb
> sp;     (925)388-0265    
>   end_of_the_skype_highlighting
> (c) (510)928-2683
> begin_of_the_skype_highlighting      &nb
> sp;     (510)928-2683    
>   end_of_the_skype_highlighting
> "building energy simulations at your fingertips"
>
>
> On 12/3/2012 6:27 AM, Chuck Khuen wrote:
>> We are now producing weather files in BIN format for pretty much 
>> anywhere outside the US at weatheranalytics.com.  Not free but simple 
>> and quick.
>> Chuck
>> _________________
>> Chuck Khuen
>> Co-Founder, EVP
>> Weather Analytics
>> weatheranalytics.com
>> 781-856-5383
>> begin_of_the_skype_highlighting      &n
>> bsp;     781-856-5383   &nbsp
>> ;  end_of_the_skype_highlighting
>>
>> *From:* Waseem Shah Khan <mailto:waseem at edsglobal.com>
>> *Sent:* Monday, December 03, 2012 1:34 AM
>> *To:* bldg-sim at lists.onebuilding.org 
>> <mailto:bldg-sim at lists.onebuilding.org>
>> *Subject:* Re: [Bldg-sim] Bldg-sim Digest, Vol 60, Issue 21 Dear 
>> Eleni,
>>
>> I am from india, Same problem with me, there is a bug in eQuest for 
>> international climate zone. it will only for US.
>>
>>
>> On Sat, Dec 1, 2012 at 2:30 AM,
>> <bldg-sim-request at lists.onebuilding.org
>> <mailto:bldg-sim-request at lists.onebuilding.org>> wrote:
>>
>>    Send Bldg-sim mailing list submissions to
>>    bldg-sim at lists.onebuilding.org 
>> <mailto:bldg-sim at lists.onebuilding.org>
>>
>>    To subscribe or unsubscribe via the World Wide Web, visit
>>    http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
>>    or, via email, send a message with subject or body 'help' to
>>    bldg-sim-request at lists.onebuilding.org
>> <mailto:bldg-sim-request at lists.onebuilding.org>
>>
>>    You can reach the person managing the list at
>>    bldg-sim-owner at lists.onebuilding.org
>> <mailto:bldg-sim-owner at lists.onebuilding.org>
>>
>>    When replying, please edit your Subject line so it is more specific
>>    than "Re: Contents of Bldg-sim digest..."
>>
>>    Today's Topics:
>>
>>       1. International Climate Zone specification
>>          (elenisoulti at co2engineering.eu
>> <mailto:elenisoulti at co2engineering.eu>)
>>
>>
>>    ---------- Forwarded message ----------
>>    From: elenisoulti at co2engineering.eu 
>> <mailto:elenisoulti at co2engineering.eu>
>>    To: "bldg-sim at lists.onebuilding.org 
>> <mailto:bldg-sim at lists.onebuilding.org>"
>>    <bldg-sim at lists.onebuilding.org <mailto:bldg-sim at lists.onebuilding.org>>,
>>    "equest-users at lists.onebuilding.org
>> <mailto:equest-users at lists.onebuilding.org>"
>>    <equest-users at lists.onebuilding.org
>> <mailto:equest-users at lists.onebuilding.org>>
>>    Cc:
>>    Date: Fri, 30 Nov 2012 20:58:48 +0000
>>    Subject: [Bldg-sim] International Climate Zone specification
>>    Dear all,
>>
>>    I am using eQUEST for a project in Spain and I have used the 
>> weather data from the
>>    EERE (Energy Efficiency & Renewable Energy) website. The climate 
>> zone described in
>>    the weather file doesn't seem to agree with the one I calculate 
>> according to the
>>    ASHRAE 90.1 description for International climate zones, based on 
>> the precipitation
>>    levels. Has anyone had any similar problems with weather data 
>> outside the US? Any
>>    suggestions about dealing with this?
>>
>>    Thank you in advance.
>>
>>    Kind regards,
>>
>>    Eleni
>>
>>    --     Eleni Soulti
>>
>>    On behalf of
>>
>>    CO2 Engineering
>>
>>    Oficina Sevilla
>>
>>    Cartuja - Edificio Marie Curie
>>
>>    C/Leonardo da Vinci 18, Planta1 3ºB
>>
>>    41092 Sevilla | España
>>
>>    T.             (0034) 679883055  
>> begin_of_the_skype_highlighting      &n
>> bsp;     (0034)
>> 679883055      end_of_the_skype_highlighting
>>       London Office
>>
>>    17, Bishops Close
>>
>>    E17 9RP London | UK
>>
>>    T.             (0044) 7969235926  
>> begin_of_the_skype_highlighting      &n
>> bsp;     (0044)
>> 7969235926      end_of_the_skype_highlighting
>>       Oficina Huelva.
>>
>>    Plaza Hermanos Costalero nº 2, 6º A
>>
>>    21001 Huelva | España
>>
>>    T.             (0034) 647143558  
>> begin_of_the_skype_highlighting      &n
>> bsp;     (0034)
>> 647143558      end_of_the_skype_highlighting
>>       w. www.co2engineering.eu <http://www.co2engineering.eu>
>>
>>    e. elenisoulti at co2engineering.eu 
>> <mailto:elenisoulti at co2engineering.eu>
>>
>>
>>
>>
>>
>>    _______________________________________________
>>    Bldg-sim mailing list
>>    Bldg-sim at lists.onebuilding.org <mailto:Bldg-sim at lists.onebuilding.org>
>>    http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
>>
>>
>>
>> --
>>
>> Kind Regards,
>>
>>
>> /Waseem Shah Khan/
>>
>> Energy Analyst
>> /Environmental Design Solutions Pvt. Ltd. /
>>
>> www.edsglobal.com <http://www.edsglobal.com/>
>>
>> *Environmental Design Solutions Pvt. Ltd. [EDS]* D - 1/25 Vasant 
>> Vihar New Delhi 110057,India
>>
>> Mob:+91.9999535880
>> begin_of_the_skype_highlighting      &n
>> bsp;     +91.9999535880   &nb
>> sp;  end_of_the_skype_highlighting
>> Tel:  +91.11.2614.7085
>> begin_of_the_skype_highlighting      &n
>> bsp;     +91.11.2614.7085   &
>> nbsp;  end_of_the_skype_highlighting
>>
>> Fax: +91 11 40568633
>>
>>
>> ---------------------------------------------------------------------
>> --------------------- _______________________________________________
>> Bldg-sim mailing list
>> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
>> To unsubscribe from this mailing list send  a blank message to 
>> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>>
>>
>> _______________________________________________
>> Bldg-sim mailing list
>> http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
>> To unsubscribe from this mailing list send  a blank message to 
>> BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
>

_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send  a blank message to BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG



More information about the Bldg-sim mailing list