The only challenge I found in modeling DHW with a hot water loop was the
incoming water temperature being based on return water temperature,
however by adjusting the DT and supply temperature on the process load I
think I've approximated it properly.
I ran two loops, one a DHW loop and one a HW loop and found them to be
within 1% of each other. Then when I switched the HW boiler over to a
condensing boiler I found a 14% savings. Finally, to verify that the
condensing boiler was operating correctly, I increased the supply T so
that the return water temp would be around 110. After doing this the
results came within 1% of each other again.
Sounds like this is the way to go for modeling a condensing boiler for
DHW.
Robby Oylear, LEEDR AP
Mechanical Engineer
direct: 206.788.4571
cell: 206.354.2721
www. <http://www.rushingco.com/> rushingco.com
From: Robby Oylear [mailto:robbyo at rushingco.com]
Sent: Tuesday, July 14, 2009 1:37 PM
To: 'bldg-sim at lists.onebuilding.org'
Subject: Condensing Boilers for DHW
With the release of eQUEST 3.63b we are given the option to model
Condensing Gas-Fired Boilers for hot water heating. However, domestic hot
water can still only be modeled by simplistic DW Heaters which have
options only for Electric, Gas, & Steam.
Would it make sense to just model the DHW loop as a HW loop with a process
load equal to the service hot water demand or is there some fundamental
reason why a hot water loop shouldn't be used as a domestic loop in
eQUEST?
Any input is appreciated. Thanks.
Robby Oylear, LEEDR AP
Mechanical Engineer
direct: 206.788.4571
cell: 206.354.2721
www. <http://www.rushingco.com> rushingco.com
Logo_B&W_1
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20090714/66e89748/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: not available
Type: image/jpeg
Size: 1804 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20090714/66e89748/attachment.jpeg>
More information about the Bldg-sim
mailing list