[Bldg-sim] Appendix G Fan Power
Nathan Miller
nathanm at rushingco.com
Thu Jul 2 08:38:02 PDT 2009
I think a lot of us were making the mistake of applying the total calculated
fan power/cfm to both the supply and return/exhaust fans (mostly due to
ambiguous wording in 90.1). Forcing the modeler to explicitly divide up the
calculated fan power allows the reviewer to more easily check that the
energy was properly accounted for.
I played around on one project and found that unsurprisingly the fan energy
didn’t change whether I put it all in supply air and none in exhaust, or
divided it up based on the relative CFMs.
Nathan Miller
Senior Energy Engineer/Mechanical Engineer
direct: 206.788.4577
fax: 206.285.7111
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of James Hess
Sent: Thursday, July 02, 2009 10:28 AM
To: Bldg-Sim
Subject: Re: [Bldg-sim] Appendix G Fan Power
We got a review comment on a recent LEED project asking us to break down the
baseline HVAC power into components even though there is no direction, or
requirement, from 90.1-2004 to do so.
Can someone please help me understand why this would be necessary?
LEED guidelines say we have to model per Appendix G, but Appendix G doesn't
say we have to do this.
I do not think it is necessary to do this as the baseline total fan energy
consumption numbers would still be the same.
The equation in Appendix G is meant to give a total allowance (for each
system) for supply, return, and exhaust fans. It doesn't matter if we break
the allowance down into components or not as the total fan energy
consumption remains the same. Therefore, there is no value in doing this.
If we did break the fan energy numbers into components, how would we do that
given that there is no direction from ASHRAE or LEED on how to do this?
Thoughts?
Regards,
James A. Hess, PE, CEM
Energy Engineer
TME, Inc.
On Jul 2, 2009, at 8:41 AM, "Jeremy Poling" <jpoling at epsteinglobal.com>
wrote:
This issue will start to become a problem for anyone running energy models
for LEED projects – reviewers on the new review teams are asking to see the
total fan power for the baseline broken into individual components and
reported as such in the template for Energy and Atmosphere Credit 1. The
90.1-2004 User’s Manual is also silent on the issue; however it raises
another issue. In the example (Example G-J on page G-28) the calculations
use total building supply CFM for an 80,000SF medical office building.
Since the baseline is System 5 in that example and there would be multiple
zones for the baseline, it appears that the equation should be used for the
whole building only and not individual systems. Is this how you are
applying the formulas? The user’s manual notes that fan powered VAV boxes
are NOT included in the total fan power number as calculated from G3.1.2.9.
Jeremy R. Poling, LEED AP
Senior Sustainability Analyst
Strategic Services
Site Solutions | Operations | Sustainability
EPSTEIN
Architecture
Interiors
Engineering
Construction
Epstein is a firm believer in sustainability. We ask that you please
consider the environment before printing this e-mail.
_____
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Ellen Franconi
Sent: Thursday, July 02, 2009 7:37 AM
To: Vikram Sami; Bldg-Sim; Michael I Rosenberg
Subject: Re: [Bldg-sim] Appendix G Fan Power
At my firm, we proportion the baseline total fan power determined as an
aggregated W/CFM based on the hp assigned to the fan motors (supply,
return, exhaust) in the design documents. Of course this assumes that your
baseline and your proposed design have a one-to-one fan correspondence.
Ellen
Ellen Franconi, Ph.D., LEED AP
Senior Energy Analyst
Architectural Energy Corporation
2540 Frontier Avenue
Boulder, CO 80301
tel. 303-444-4149
fax 303-444-4303
efranconi at archenergy.com
http://www.archenergy.com/
>>> "Rosenberg, Michael I" <michael.rosenberg at pnl.gov> 7/1/2009 4:48 PM >>>
You have calculated the kW/cfm correctly according to the 2004 version of
Appendix G. The allowance actually goes up a little in 2007, for your case.
As for the second part of your question, no you do not apply the same kW/cfm
to the exhaust fan. The calculated allowed fan power the total allowed power
for all fans that are part of the system, including the exhaust fan. The cfm
component is based on the supply fan cfm only. Unfortunately, Appendix G
gives no direction on how to divide the allowed fan power up among the
various fans in the system.
Mike
__________________________
Michael Rosenberg
Senior Commercial Buildings Energy Analyst
ENERGY & ENVIRONMENT DIRECTORATE
Pacific Northwest National Laboratory
2032 Todd Street
Eugene, OR 97405
(541) 844-1960
michael.rosenberg at pnl.gov
www.pnl.gov
From: bldg-sim-bounces at lists.onebuilding.org
[mailto:bldg-sim-bounces at lists.onebuilding.org] On Behalf Of Vikram Sami
Sent: Wednesday, July 01, 2009 3:03 PM
To: Bldg-Sim
Subject: [Bldg-sim] Appendix G Fan Power
G3.1.2.9 Gives you a formula for calculating system fan electrical power for
supply, return, exhaust and relief. Lets sat I have a zone with a PSZ-HP
that has a supply volume of 1500 cfm. Using this formula along with table
G3.1.2.9 I get a fan horse power of 1.29 and kW of 1.17. This equates to
0.00078 kW/cfm – which seems really high.
The second part to my question is assuming I have 500cfm of exhaust in this
zone, do I apply the same kW/cfm to the exhaust fans as well as the return
fans? It seems that the lower the fan volume the more inefficient the
Appendix G values get from these tables.
Any guidance would be much appreciated.
Vikram Sami, LEED AP
Direct Phone 404-253-1466 | Direct Fax 404-253-1366
LORD, AECK & SARGENT ARCHITECTURE
1201 Peachtree Street NE, Suite 300, Atlanta, GA 30361
Responsive Design · Technological Expertise · Exceptional Service
Please visit our new website | <file:///\\www.lordaecksargent.com\>
www.lordaecksargent.com
P Think GREEN before you print.
_______________________________________________
Bldg-sim mailing list
http://lists.onebuilding.org/listinfo.cgi/bldg-sim-onebuilding.org
To unsubscribe from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20090702/b68d799f/attachment.htm>
More information about the Bldg-sim
mailing list