[BLDG-SIM] New Calculation method for Baseline Fan Energyin Addendum R
Bill Talbert
btalbert at aeieng.com
Thu Oct 25 09:20:02 PDT 2007
LEED has approved the use of addenda to A90.1-2004 so Addendum 'ac' can
be applied. The change to the Appendix G fan power formula was not
included in an addendum because it occurred while 90.1 was still
considered 'informative,' not 'normative,' as the currently proposed
Addendum 'r' to A90.1-2007 is proposing to change. I believe the change
to the fan power formula, however, was approved by LEED in a CIR, so you
should be able to apply the new formula and pressure credits for the
Appendix G PRM.
Bill
Bill Talbert, PE, LEED® AP
Mechanical Systems
Phone: (608) 441-6677
E-mail: btalbert at aeieng.com
Affiliated Engineers Inc.
5802 Research Park Blvd.
Madison, WI. 53719
Tel. (608) 238-2616
Fax. (608) 238-2614
>>> "Baker, Kristopher" <kbaker at syska.com> 10/25/2007 10:47 AM >>>
Any ideas if we can apply the new methodology, indicated in either
Addenda ac for the 2004 version or addenda r for the 2007 version, to
the Appendix G Performance Rating Method?
KB
Kristopher S. Baker, PE
LEED(r) Accredited Professional
Associate
Senior Sustainability Specialist - Sustainable Design &
High Performance Building Technology
Syska Hennessy Group, Inc.
Tel: 703.629.8028
Direct Fax: 866.885.5621
Email: kbaker at syska.com
http://www.syska.com ( http://www.syska.com/ )
P Please consider the environment before printing this e-mail
________________________________
This email and any files transmitted with it are the property of Syska
Hennessy Group and are intended solely for the use of the individual
or
entity to which they are addressed. The information contained herein
may
include trade secrets or privileged or otherwise confidential
information and unauthorized review, forwarding, printing,
distributing,
or using such information is strictly prohibited and may be unlawful.
If
you received this message in error, or have reason to believe you are
not authorized to receive it, please promptly delete this message and
notify the sender by e-mail.
________________________________
-----Original Message-----
From: BLDG-SIM at gard.com [mailto:BLDG-SIM at gard.com] On Behalf Of
Michael
Rosenberg
Sent: Wednesday, October 24, 2007 10:03 PM
To: BLDG-SIM at gard.com
Cc: sferguson at ashrare.org
Subject: [BLDG-SIM] New Calculation method for Baseline Fan Energyin
Addendum R
Mike and Andrew,
That is Addendum R that Andrew is referring to. It is actually
Addendum
R to 90.1, 2007. Even though 2007 has not been published yet, ASHRAE
is
already up to Addendum R. As for the calculation, Andrew made a good
catch. It is a typo and should read CFM x 0.00094 + A and CFM x
0.0013 + A.
Mike
Michael Rosenberg
Oregon Department of Energy
625 Marion St. N.E.
Salem, OR 97301-3742
Phone : (503) 373-7809
Fax: (503) 373-7806
>>> "Michael Tillou" <michael.tillou at gmail.com> 10/24/2007 11:39:01 AM
>>>
I think you mean to be referencing ASHRAE 90.1-2004 addendum ac not
addendum
r which includes two new methods for calculating fan power limits.
The
first looks at total Motor HP which isn't very useful for energy
modeling
purposes and the second looks at fan brake-horsepower. The fan
brake-horsepower equations are "(CFM x 0.00094) + A" and "(CFM x
0.0013) +
A" for constant volume and variable volume systems respectively. CFM
is
the
design airflow rate and A is the brakehorse power adjustement for
various
pressure drop adjustments given in Table 6.5.3.1.1B.
Mike
Michael Tillou, PE, LEED
Tillou Engineering, LLC
Williamstown, MA 01267
P: 413-458-9870 C: 413-652-1087
_____
From: BLDG-SIM at gard.com [mailto:BLDG-SIM at gard.com] On Behalf Of Andrew
Craig
Sent: Wednesday, October 24, 2007 11:56 AM
To: BLDG-SIM at gard.com
Subject: [BLDG-SIM] New Calculation method for Baseline Fan Energy in
Addendum R
I was wondering if anyone out there can explain the new calculation
shown
for baseline fan brake horsepower in Table G3.1.2.9 of Addendum R to
ASHRAE
90.1-2004? At first glance, the equation doesn't make sense because
you
are
subtracting a relatively small number (0.0013+A) from a large number
(CFMs)
leaving you with a ridiculously large baseline fan motor brake
horsepower.
Am I just reading this wrong or is there a typo? Isn't there an
easier
way
out there to calculate baseline fan energy (please see version 1 of
Appendix
G for another confusing calculation)?
Andrew Craig, EIT, LEEDR AP | Mechanical Designer
INTERFACE ENGINEERING
708 SW Third Avenue | Suite 400 | Portland, OR 97204
direct: 503.382.2696
office: 503.382.2266
fax: 503.382.2262
email: Andrew_C at ieice.com
web: www.ieice.com
Consultants of Choice to the Built Environment for over 35 years
Kirkland, WA | Portland, OR | Sacramento, CA | Salem, OR |
SanFrancisco,
CA
==================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
======================================================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
==================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
=====================================================You received this
e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
======================================================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20071025/46ef3165/attachment.htm>
More information about the Bldg-sim
mailing list