[BLDG-SIM] Huge heating demand
Vikram Sami
VSami at lasarchitect.com
Fri Jun 22 09:26:57 PDT 2007
I'm not sure that's unreasonable - especially for a building of that
size (210 ft2) - the skin loads are pretty significant. There also seems
to be a large glazing area. Looking at weather charts for London, the
summers are really mild (highs in the upper 70s is a non existent summer
for a lot of places), so for a skin dominated building, your loads
wouldn't be that high. The winters are pretty cold though.
I guess it depends on how you modeled your internal heat gain (lights,
equipment, people) , outside air changes and infiltration rates. If you
are trying to model a small room in a larger building, then you might
want to make sure you have the internal walls modeled adiabatically (or
some other appropriate way). Looking at the balance point temperature
would also be a good gut check.
Vikram Sami, LEED AP
Direct Phone 404-253-1466 | Direct Fax 404-253-1366
LORD, AECK & SARGENT ARCHITECTURE
1201 Peachtree Street NE, Suite 300, Atlanta, GA 30361
Responsive Design * Technological Expertise * Exceptional Service
www.lordaecksargent.com
Please don't print this email unless you really have to.
In the United States, we use enough office paper each year to build a
10-foot high wall that's 6,815 miles long or two and a half times the
distance from New York to Los Angeles.
~ Wisconsin Department of Natural Resources, "Recycling Facts and
Figures," PUBL CE-163, 2002.
________________________________
From: BLDG-SIM at gard.com [mailto:BLDG-SIM at gard.com] On Behalf Of Kevin
Burke
Sent: Friday, June 22, 2007 11:29 AM
To: BLDG-SIM at gard.com
Subject: [BLDG-SIM] Huge heating demand
Hi All,
I'm running a 210 ft2 room in eQuest and have assigned generic fabric
spec and a fan coil system with baseboard heating and the location is
London. One of the facades is glazing. When looking at the demand
summary the heating demand is massive relative to all other energy
demands (4 times greater than cooling demand in Summer!). Could anyone
suggest what I might be doing wrong? I've looked at air flow rates,
u-values, glazing and nothing seems to reduce it to what may be
expected.
Kind Regards,
Kevin Burke
____________________________________________________________
Electronic mail messages entering and leaving Arup business
systems are scanned for acceptability of content and viruses
==================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
===========================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20070622/1fe1b64c/attachment.htm>
More information about the Bldg-sim
mailing list