[BLDG-SIM] Simulating in-suite HRV's on FC type systems using eQUEST
Brian Fountain
greensim at lara.on.ca
Wed Dec 10 13:15:03 PST 2003
I am using eQUEST to model a high-rise multi-unit residential building (in a
cold climate). The mechanical system most likely for selection will include
2-pipe fan coils (with a supplementary electric coil) in the suites and a
corridor make-up air unit. The in-suite fan coils under consideration have
an outdoor air intake and an air-to-air heat exchanger to recover heat from
the suite washroom exhaust. This is not how the FC fan coil system is set
up in DOE 2.2 - and there is no provision for heat recovery at the fan-coil
level. I am using the OA-FROM-SYS keyword which moves the entire
ventilation load to the corridor make-up air system where heat recovery can
be applied. Doing this appears to greatly improve the energy performance of
the building. I am wondering if modeling the system in this was is
over-stating performance of the heat recovery.
I am wondering if there is experience within the group to better model such
a system. Any assistance would be greatly appreciated.
Kind regards,
Brian Fountain, P.Eng.
Energy Engineer
GreenSim
(905)639-6014 -- voice
(905)639-0443 -- fax
bfountain at canada.com
===========================
You received this e-mail because you are subscribed
to the BLDG-SIM at GARD.COM mailing list. To unsubscribe
from this mailing list send a blank message to
BLDG-SIM-UNSUBSCRIBE at GARD.COM
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/bldg-sim-onebuilding.org/attachments/20031210/ce18e271/attachment.htm>
More information about the Bldg-sim
mailing list